    Hi All,

    I’m in the process of a complete kitchen refit so will be recabling the entire thing. I understand about grouping dimmers in the app but do I just wire the two switches in parallel?

    I’ve attached an image to show what I mean – I hope it is visible!

    Dave

    Attachments:
    You must be logged in to view attached files.
    #25254
     Chester says:

    Chester
    Participant

    By the looks of the L21 manual, there are more than one ways to skin this cat. You do indeed wire the second L21 in parallel (so live and switches live connections are identical), but the second L21 sends a radio signal to control the first one. You could also wire them individually into 2 independent light circuits and group them together in the app.

    Caveat – I’ve yet to venture into Gen2 ownership, so I’m going by what the manual says!

    Chester
    #25256
     David says:

    David
    Participant

    Co-incidentally, I spoke to a very helpful chap from the company yesterday and he confirmed your/my thoughts, although he suggested it would be wise to provide a three core+earth wire rather than twin+earth between the switches as it would then be easy to revert to conventional switches should it be necessary.

    Splitting into more than one group is an idea worth considering – thanks for that