2 gang dimmer tripping RCD

LightwaveRF Communi… > Forum > Installation and… > 2 gang dimmer tripp…

This topic contains 1 reply, has 2 voices, and was last updated by  btidey 2 months, 2 weeks ago.

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #56874
     ALQ_82 says:

    ALQ_82
    Participant

    Hi, I have installed several dimmers around the house without issue, but having a spot of trouble.

    I have a 2 gang dimmer, that trips the RCD as soon as I put the power back on. Each gang is controlling a circuit that are on different RCDs on the consumer unit.
    I see the whole switch is powered by the supply into the primary gang, rather than each gang being isolated, so I suspect that this is causing the fault. Can someone advise me if this set up is even possible.

    Cheers, AL_Q.

    #56875
     btidey says:

    btidey
    Participant

    RCD works by ensuring the live current is exactly balanced by the returning neutral current. If it is out by 20mA or so then it trips.

    Once you share the neutrals of different RCDs at the switch then this is not necessarily the case and the RCD likely trips.

    So, you should not try to use the same shared dimmer switch to control circuits from different RCDs.

    One method would be to use in-line dimmers and put a 2 gang wire-free switch in place to control them.

    https://lightwaverf.com/collections/all/products/wire-free-in-line-dimmer-kits